Temp does have something to do with it. At higher outside temps ac runs
higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're probably
not qualified to go any deeper.

"John H." wrote in message
...
On Mon, 15 Sep 2008 19:41:33 -0400, DK wrote:

John H. wrote:
Gone four days and back to 853 messages. Over 300 from one individual.

Had a great time at Virginia Beach. Saw lots of boats. Will post
pictures
of some when I get the chance.

Air conditioner kept popping the circuit breaker when the temp was
hovering
around 95 yesterday.

Anyone know anything about air conditioners?


Sure. They remove heat from your house, car, boat, etc.

The temperature has nothing to do with your problem. Something else is
in need of a replacement.


Then why did it work in the evening, and all morning when the temperature
was lower?

Don't even tell me it has something to do with Global Warming!
--
John H.



  #2   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Jul 2008
Posts: 8,663
Default Holy ****!

On Mon, 15 Sep 2008 20:40:16 -0400, "jamesgangnc" wrote:

Temp does have something to do with it. At higher outside temps ac runs
higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're probably
not qualified to go any deeper.


Thanks for getting back to me. I've thought of the circuit breaker, but
couldn't find one yesterday. Then I rationalized that it couldn't be the
breaker because it ran at other times. I didn't know they would draw more
when the weather was hot.

The park was almost empty, so the brownout idea probably wouldn't apply.
The trailer is this year's model, and I've had it only two and a half
months. I'll try the circuit breaker replacement if the dealer says he
can't find a problem.
--
John H.
  #3   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Jul 2006
Posts: 5,091
Default Holy ****!


"jamesgangnc" wrote in message
m...
Temp does have something to do with it. At higher outside temps ac runs
higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're
probably not qualified to go any deeper.



Exactly. The problem with these rigs when used in travel trailers is the
poor insulation of the trailer itself. On hot days the temperature can rise
back up over the thermostat setpoint before the head pressure bleeds off.

But, I am willing to be his problem was low RV park voltage.

Eisboch


  #4   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Sep 2008
Posts: 94
Default Holy ****!

Eisboch wrote:
"jamesgangnc" wrote in message
m...
Temp does have something to do with it. At higher outside temps ac runs
higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're
probably not qualified to go any deeper.



Exactly. The problem with these rigs when used in travel trailers is the
poor insulation of the trailer itself. On hot days the temperature can rise
back up over the thermostat setpoint before the head pressure bleeds off.

But, I am willing to be his problem was low RV park voltage.

Eisboch


That's what I said yesterday. Congratulations.
  #5   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Sep 2008
Posts: 3
Default Holy ****!

On Tue, 16 Sep 2008 09:32:21 -0400, "Eisboch" wrote:


"jamesgangnc" wrote in message
om...
Temp does have something to do with it. At higher outside temps ac runs
higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're
probably not qualified to go any deeper.



Exactly. The problem with these rigs when used in travel trailers is the
poor insulation of the trailer itself. On hot days the temperature can rise
back up over the thermostat setpoint before the head pressure bleeds off.

But, I am willing to be his problem was low RV park voltage.

Eisboch


I'm hoping you're correct!

But, I'll probably never know for sure. Maybe the dealer will find a
bad capacitor or something. But I'm going to change the circuit
breaker first.


  #6   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Aug 2008
Posts: 174
Default Holy ****!

John H. wrote:
On Tue, 16 Sep 2008 09:32:21 -0400, "Eisboch" wrote:

"jamesgangnc" wrote in message
m...
Temp does have something to do with it. At higher outside temps ac runs
higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're
probably not qualified to go any deeper.


Exactly. The problem with these rigs when used in travel trailers is the
poor insulation of the trailer itself. On hot days the temperature can rise
back up over the thermostat setpoint before the head pressure bleeds off.

But, I am willing to be his problem was low RV park voltage.

Eisboch


I'm hoping you're correct!

But, I'll probably never know for sure. Maybe the dealer will find a
bad capacitor or something. But I'm going to change the circuit
breaker first.


Easter egg hunting is not a good troubleshooting method, and it could
get costly.

You need a good multimeter that is capable of reading at least 30 amps
AC and AC volts. Keep in mind amps are read in series. Meaning you have
to break open a circuit or use a clamp on pickup or if the Air
Conditioner unit plugs into an outlet, instead of being hardwired, you
can use an adapter with the clamp on pickup or a killowatt type of
device to take readings.




  #7   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Jul 2006
Posts: 5,091
Default Holy ****!


"jim" wrote in message
...
John H. wrote:
On Tue, 16 Sep 2008 09:32:21 -0400, "Eisboch" wrote:

"jamesgangnc" wrote in message
m...
Temp does have something to do with it. At higher outside temps ac
runs higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're
probably not qualified to go any deeper.


Exactly. The problem with these rigs when used in travel trailers is
the poor insulation of the trailer itself. On hot days the temperature
can rise back up over the thermostat setpoint before the head pressure
bleeds off.

But, I am willing to be his problem was low RV park voltage.

Eisboch


I'm hoping you're correct!

But, I'll probably never know for sure. Maybe the dealer will find a
bad capacitor or something. But I'm going to change the circuit
breaker first.


Easter egg hunting is not a good troubleshooting method, and it could get
costly.

You need a good multimeter that is capable of reading at least 30 amps AC
and AC volts. Keep in mind amps are read in series. Meaning you have to
break open a circuit or use a clamp on pickup or if the Air Conditioner
unit plugs into an outlet, instead of being hardwired, you can use an
adapter with the clamp on pickup or a killowatt type of device to take
readings.




Heh .... I drafted a post for John, describing the old Navy "Easter Egging"
technique of troubleshooting,
and recommended he do a more logical series of tests, but then I realized
that people need to do what they need to do, so I deleted the post.

I doubt very much his circuit breaker is bad. Could be wrong, but there are
other things I'd check first.

But, I have a feeling he's going to claim the problem as being fixed after
he replaces it. For a while. Then, sometime in the future when conditions
are similar to that he wrote about, the problem will return.

Eisboch


  #8   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Sep 2008
Posts: 3
Default Holy ****!

On Tue, 16 Sep 2008 11:01:06 -0400, "Eisboch" wrote:


"jim" wrote in message
...
John H. wrote:
On Tue, 16 Sep 2008 09:32:21 -0400, "Eisboch" wrote:

"jamesgangnc" wrote in message
m...
Temp does have something to do with it. At higher outside temps ac
runs higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're
probably not qualified to go any deeper.


Exactly. The problem with these rigs when used in travel trailers is
the poor insulation of the trailer itself. On hot days the temperature
can rise back up over the thermostat setpoint before the head pressure
bleeds off.

But, I am willing to be his problem was low RV park voltage.

Eisboch

I'm hoping you're correct!

But, I'll probably never know for sure. Maybe the dealer will find a
bad capacitor or something. But I'm going to change the circuit
breaker first.


Easter egg hunting is not a good troubleshooting method, and it could get
costly.

You need a good multimeter that is capable of reading at least 30 amps AC
and AC volts. Keep in mind amps are read in series. Meaning you have to
break open a circuit or use a clamp on pickup or if the Air Conditioner
unit plugs into an outlet, instead of being hardwired, you can use an
adapter with the clamp on pickup or a killowatt type of device to take
readings.




Heh .... I drafted a post for John, describing the old Navy "Easter Egging"
technique of troubleshooting,
and recommended he do a more logical series of tests, but then I realized
that people need to do what they need to do, so I deleted the post.

I doubt very much his circuit breaker is bad. Could be wrong, but there are
other things I'd check first.

But, I have a feeling he's going to claim the problem as being fixed after
he replaces it. For a while. Then, sometime in the future when conditions
are similar to that he wrote about, the problem will return.

Eisboch


Give me a break! I don't usually make a lot of claims that aren't
true. Perhaps you're confusing me with someone else.

The new circuit breaker costs $12 bucks. I won't know if that's the
problem until we get another 95 degree day. If the problem returns,
then I'll know it wasn't the circuit breaker.

Unlike some other folks, I have no problem with being wrong. If the
problem reoccurs, I'll let you know.
  #9   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Jul 2006
Posts: 10,492
Default Holy ****!

On Tue, 16 Sep 2008 13:15:01 -0400, John H.
wrote:

Unlike some other folks, I have no problem with being wrong. If the
problem reoccurs, I'll let you know.


As others have mentioned, the two most likely causes are either low
voltage or insufficient anti-cycling delay in the condenser
controller.

Excessive cycling can be caused by poor air flow among other things -
clogged filter, fan speed too low, etc.

  #10   Report Post  
posted to rec.boats
external usenet poster
 
First recorded activity by BoatBanter: Sep 2008
Posts: 2
Default Holy ****!

John H. wrote:
On Tue, 16 Sep 2008 11:01:06 -0400, "Eisboch" wrote:

"jim" wrote in message
...
John H. wrote:
On Tue, 16 Sep 2008 09:32:21 -0400, "Eisboch" wrote:

"jamesgangnc" wrote in message
m...
Temp does have something to do with it. At higher outside temps ac
runs higher pressures. Takes more current to start the compressor. AC
copmpressors have to start under a load so they need a lot of current
initially. First make sure you have the correct circuit breaker. Then
replace if it's old it cause when they get old they blow at lower than
rated. Voltage brownout will do it as well. Check and tighten all the
connections. None of that works call the service guy cause you're
probably not qualified to go any deeper.

Exactly. The problem with these rigs when used in travel trailers is
the poor insulation of the trailer itself. On hot days the temperature
can rise back up over the thermostat setpoint before the head pressure
bleeds off.

But, I am willing to be his problem was low RV park voltage.

Eisboch
I'm hoping you're correct!

But, I'll probably never know for sure. Maybe the dealer will find a
bad capacitor or something. But I'm going to change the circuit
breaker first.
Easter egg hunting is not a good troubleshooting method, and it could get
costly.

You need a good multimeter that is capable of reading at least 30 amps AC
and AC volts. Keep in mind amps are read in series. Meaning you have to
break open a circuit or use a clamp on pickup or if the Air Conditioner
unit plugs into an outlet, instead of being hardwired, you can use an
adapter with the clamp on pickup or a killowatt type of device to take
readings.



Heh .... I drafted a post for John, describing the old Navy "Easter Egging"
technique of troubleshooting,
and recommended he do a more logical series of tests, but then I realized
that people need to do what they need to do, so I deleted the post.

I doubt very much his circuit breaker is bad. Could be wrong, but there are
other things I'd check first.

But, I have a feeling he's going to claim the problem as being fixed after
he replaces it. For a while. Then, sometime in the future when conditions
are similar to that he wrote about, the problem will return.

Eisboch


Give me a break! I don't usually make a lot of claims that aren't
true. Perhaps you're confusing me with someone else.

The new circuit breaker costs $12 bucks. I won't know if that's the
problem until we get another 95 degree day. If the problem returns,
then I'll know it wasn't the circuit breaker.

Unlike some other folks, I have no problem with being wrong. If the
problem reoccurs, I'll let you know.


I think he meant because of cooler weather, you will think it is cured.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is Off
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Oh, shit. It happened to me. Roger Long Cruising 15 July 8th 06 12:04 AM
HOLY SHIT! Joe ASA 0 November 9th 05 03:41 AM
I smell Cat Shit Jonathan Ganz ASA 4 August 6th 03 05:48 PM
Bob = Cat SHIT SkitchNYC ASA 3 July 19th 03 10:48 PM
Need to pump shit? Peggie Hall General 8 July 17th 03 12:31 AM


All times are GMT +1. The time now is 01:23 AM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 BoatBanter.com.
The comments are property of their posters.
 

About Us

"It's about Boats"

 

Copyright © 2017