engsol
 
Posts: n/a
Default On-board generators Revisited

I spnt a bit of web time googling marine battery chargers that
might work with the Honda EU1000 or EU2000 generators.

Here are some URLs...not an exhaustive list by any means...
http://www.charlesindustries.com/main/ma_chargers.html
http://www.newmarpower.com/
http://www.mastervolt.com/chargers/index.asp
http://www.progressivedyn.com/
http://www.majorpower.com/newmar/p3bc.html (interesting)
http://www.batterystuff.com/battery/...o/dual-pro.htm

I like the specs shown by majorpower.com. They give a
figure for power factor, which sems to be missing from
other manufs.

As a trial...assume a 100 AH gel battery. A PT14 charger will
charge 28 to 140 AH batteries at 14 amps maximum. 14 amps times
1.1 (efficeincy of 90%) times PF of .95 (spec at 115VAC) equals
about 16.2 amps. Adjust to 115VAC input and you get about 2 amps,
or 230 VA. A 25 amp charger might work even better without over
stressing the generator.
I called a couple of the charger manufs, and they concur
with the numbers. The trick is to get a charger with a rated output
compatible with the available input power. A 150 amp charger ain't
going to work with a EU1000. But of course the trade-off is longer
charge times.

Hope this helps.
Norm B

  #2   Report Post  
Doug Dotson
 
Posts: n/a
Default On-board generators Revisited

I'm confused about why there is some question about
running a battery charger off of a genset. I have run
mine for several years with no problem. The battery charger
runs off the genset the same as off of shore power.

Doug
s/v Callista

"engsol" wrote in message
...
I spnt a bit of web time googling marine battery chargers that
might work with the Honda EU1000 or EU2000 generators.

Here are some URLs...not an exhaustive list by any means...
http://www.charlesindustries.com/main/ma_chargers.html
http://www.newmarpower.com/
http://www.mastervolt.com/chargers/index.asp
http://www.progressivedyn.com/
http://www.majorpower.com/newmar/p3bc.html (interesting)
http://www.batterystuff.com/battery/...o/dual-pro.htm

I like the specs shown by majorpower.com. They give a
figure for power factor, which sems to be missing from
other manufs.

As a trial...assume a 100 AH gel battery. A PT14 charger will
charge 28 to 140 AH batteries at 14 amps maximum. 14 amps times
1.1 (efficeincy of 90%) times PF of .95 (spec at 115VAC) equals
about 16.2 amps. Adjust to 115VAC input and you get about 2 amps,
or 230 VA. A 25 amp charger might work even better without over
stressing the generator.
I called a couple of the charger manufs, and they concur
with the numbers. The trick is to get a charger with a rated output
compatible with the available input power. A 150 amp charger ain't
going to work with a EU1000. But of course the trade-off is longer
charge times.

Hope this helps.
Norm B



  #3   Report Post  
Kelton
 
Posts: n/a
Default On-board generators Revisited

Doug,
you probably have a battery charger that puts out fewer watts that your
generator supplies. If you have a battery charger that is trying to
supply 100 amps to the batteries (1200 watts) and the generator can only
supply 1000 watts, you have a problem. If you have discovered a way to
do this, let me know. We will apply for a patent for perpetual motion.
Kelton
s/v Isle Escape

Doug Dotson wrote:
I'm confused about why there is some question about
running a battery charger off of a genset. I have run
mine for several years with no problem. The battery charger
runs off the genset the same as off of shore power.

Doug
s/v Callista

"engsol" wrote in message
...

I spnt a bit of web time googling marine battery chargers that
might work with the Honda EU1000 or EU2000 generators.

Here are some URLs...not an exhaustive list by any means...
http://www.charlesindustries.com/main/ma_chargers.html
http://www.newmarpower.com/
http://www.mastervolt.com/chargers/index.asp
http://www.progressivedyn.com/
http://www.majorpower.com/newmar/p3bc.html (interesting)
http://www.batterystuff.com/battery/...o/dual-pro.htm

I like the specs shown by majorpower.com. They give a
figure for power factor, which sems to be missing from
other manufs.

As a trial...assume a 100 AH gel battery. A PT14 charger will
charge 28 to 140 AH batteries at 14 amps maximum. 14 amps times
1.1 (efficeincy of 90%) times PF of .95 (spec at 115VAC) equals
about 16.2 amps. Adjust to 115VAC input and you get about 2 amps,
or 230 VA. A 25 amp charger might work even better without over
stressing the generator.
I called a couple of the charger manufs, and they concur
with the numbers. The trick is to get a charger with a rated output
compatible with the available input power. A 150 amp charger ain't
going to work with a EU1000. But of course the trade-off is longer
charge times.

Hope this helps.
Norm B





  #4   Report Post  
Jeff Morris
 
Posts: n/a
Default On-board generators Revisited

Actually, I'd be happy to get 50 or 60 Amps, but some of the advice seems to be
25 Amps might be all I might expect. But the need is for 100 Amps-Hours or
more, so a low current charger is not a good solution if I have to run the
genset 4 hours a day.


"Kelton" wrote in message
.. .
Doug,
you probably have a battery charger that puts out fewer watts that your
generator supplies. If you have a battery charger that is trying to
supply 100 amps to the batteries (1200 watts) and the generator can only
supply 1000 watts, you have a problem. If you have discovered a way to
do this, let me know. We will apply for a patent for perpetual motion.
Kelton
s/v Isle Escape

Doug Dotson wrote:
I'm confused about why there is some question about
running a battery charger off of a genset. I have run
mine for several years with no problem. The battery charger
runs off the genset the same as off of shore power.

Doug
s/v Callista

"engsol" wrote in message
...

I spnt a bit of web time googling marine battery chargers that
might work with the Honda EU1000 or EU2000 generators.

Here are some URLs...not an exhaustive list by any means...
http://www.charlesindustries.com/main/ma_chargers.html
http://www.newmarpower.com/
http://www.mastervolt.com/chargers/index.asp
http://www.progressivedyn.com/
http://www.majorpower.com/newmar/p3bc.html (interesting)
http://www.batterystuff.com/battery/...o/dual-pro.htm

I like the specs shown by majorpower.com. They give a
figure for power factor, which sems to be missing from
other manufs.

As a trial...assume a 100 AH gel battery. A PT14 charger will
charge 28 to 140 AH batteries at 14 amps maximum. 14 amps times
1.1 (efficeincy of 90%) times PF of .95 (spec at 115VAC) equals
about 16.2 amps. Adjust to 115VAC input and you get about 2 amps,
or 230 VA. A 25 amp charger might work even better without over
stressing the generator.
I called a couple of the charger manufs, and they concur
with the numbers. The trick is to get a charger with a rated output
compatible with the available input power. A 150 amp charger ain't
going to work with a EU1000. But of course the trade-off is longer
charge times.

Hope this helps.
Norm B







  #5   Report Post  
Doug Dotson
 
Posts: n/a
Default On-board generators Revisited

No, that's pretty much obvious. Don't know why anyone would
waste their time working around it.

Doug
s/v Callista

"Kelton" wrote in message
.. .
Doug,
you probably have a battery charger that puts out fewer watts that your
generator supplies. If you have a battery charger that is trying to
supply 100 amps to the batteries (1200 watts) and the generator can only
supply 1000 watts, you have a problem. If you have discovered a way to
do this, let me know. We will apply for a patent for perpetual motion.
Kelton
s/v Isle Escape

Doug Dotson wrote:
I'm confused about why there is some question about
running a battery charger off of a genset. I have run
mine for several years with no problem. The battery charger
runs off the genset the same as off of shore power.

Doug
s/v Callista

"engsol" wrote in message
...

I spnt a bit of web time googling marine battery chargers that
might work with the Honda EU1000 or EU2000 generators.

Here are some URLs...not an exhaustive list by any means...
http://www.charlesindustries.com/main/ma_chargers.html
http://www.newmarpower.com/
http://www.mastervolt.com/chargers/index.asp
http://www.progressivedyn.com/
http://www.majorpower.com/newmar/p3bc.html (interesting)
http://www.batterystuff.com/battery/...o/dual-pro.htm

I like the specs shown by majorpower.com. They give a
figure for power factor, which sems to be missing from
other manufs.

As a trial...assume a 100 AH gel battery. A PT14 charger will
charge 28 to 140 AH batteries at 14 amps maximum. 14 amps times
1.1 (efficeincy of 90%) times PF of .95 (spec at 115VAC) equals
about 16.2 amps. Adjust to 115VAC input and you get about 2 amps,
or 230 VA. A 25 amp charger might work even better without over
stressing the generator.
I called a couple of the charger manufs, and they concur
with the numbers. The trick is to get a charger with a rated output
compatible with the available input power. A 150 amp charger ain't
going to work with a EU1000. But of course the trade-off is longer
charge times.

Hope this helps.
Norm B









  #6   Report Post  
Rick & Linda Bernard
 
Posts: n/a
Default On-board generators Revisited

It is actually worst then that. Gensets put out volts and amps. The
combination of the two is KVA not KW. Gensets are rated on KVA not KW. To
get KW you multiply KVA by the power factor. A lot of manufactures assume a
power factor of 1 and do this conversion for you. But in reality you seldom
have a power factor of 1. By the way 1 is the best it can be.

Power factor is a measure of the phase shift of volts to current. The
things that cause a phase shift are inductive loads. Things like
transformers, airconditioner compressors, fans, electric drills, or a
battery charger (marine units are typically transformer isolated).
Resistive loads like resistance heaters do not cause a phase shift. The
inductive loads provide work by building and colapsing magentic fields.
These fields requires some reverse voltage (back EMF) to compeletly colapse
the field prior to building it in the oppsite direction. The back EMF
causes the shift in voltage and current. To fight this engineers add
capacitors to store some energy to counter this back EMF.

Capacitors increase size and cost money. Not a lot but some. In this
competive market most of us would buy a $1000 airconditioner vs a $1200
slightly larger AC. That said; I wish that the builders would offer power
factor correction capacitors as an option. Then the folks with gensets
could choose. (Mermaid A/C might by power factor corrected)

You can add capacitors to adjust you power factor but it is complicated,
requires test equipment that few people own, and requires disassembly of the
electrical devices to properally install. If you add to much capacitance
you can damage the genset. This requires the capacitance to come on when
the load comes on. Therefore it must be mounted at the load after its
on-off switch. Not a job for the weekend boaters but for a highly skilled
electrician who does this sort of thing. Not to many people do it so not to
many electricans do it. Why should they invest thousands in test equipment
for something they may never do in their lifetime.

Just a guess but some boats may lose 20% or more of their genset capacity to
lousy power factor.

For genset sizing I like to use the x2 factor (minimum). Add up all your
loads and x2 to get the genset size. Remember to start the biggest load
first. When adding up loads look at the input power not the output power.
A 100 amp battery charger may have an output of 100*12 = 1200 watts but the
input power can ge significantly higher. It would not suprise me if it was
15 amps worst case. That's 1.8 KVA. I don't think that this type of load
requires a high surge (or a high sudden in-rush) to start up so the x2
factor would oversize. But I would think that the Honda 2000 would be wide
open if your charger is pulling 100 amps.

Sometimes power factor gets worse a load drops so don't expect the Honda to
have an easy time it the charger is putting out 50 amps.

"Kelton" wrote in message
.. .
Doug,
you probably have a battery charger that puts out fewer watts that your
generator supplies. If you have a battery charger that is trying to
supply 100 amps to the batteries (1200 watts) and the generator can only
supply 1000 watts, you have a problem. If you have discovered a way to
do this, let me know. We will apply for a patent for perpetual motion.
Kelton
s/v Isle Escape

Doug Dotson wrote:
I'm confused about why there is some question about
running a battery charger off of a genset. I have run
mine for several years with no problem. The battery charger
runs off the genset the same as off of shore power.

Doug
s/v Callista

"engsol" wrote in message
...

I spnt a bit of web time googling marine battery chargers that
might work with the Honda EU1000 or EU2000 generators.

Here are some URLs...not an exhaustive list by any means...
http://www.charlesindustries.com/main/ma_chargers.html
http://www.newmarpower.com/
http://www.mastervolt.com/chargers/index.asp
http://www.progressivedyn.com/
http://www.majorpower.com/newmar/p3bc.html (interesting)
http://www.batterystuff.com/battery/...o/dual-pro.htm

I like the specs shown by majorpower.com. They give a
figure for power factor, which sems to be missing from
other manufs.

As a trial...assume a 100 AH gel battery. A PT14 charger will
charge 28 to 140 AH batteries at 14 amps maximum. 14 amps times
1.1 (efficeincy of 90%) times PF of .95 (spec at 115VAC) equals
about 16.2 amps. Adjust to 115VAC input and you get about 2 amps,
or 230 VA. A 25 amp charger might work even better without over
stressing the generator.
I called a couple of the charger manufs, and they concur
with the numbers. The trick is to get a charger with a rated output
compatible with the available input power. A 150 amp charger ain't
going to work with a EU1000. But of course the trade-off is longer
charge times.

Hope this helps.
Norm B







  #7   Report Post  
Wayne.B
 
Posts: n/a
Default On-board generators Revisited

On Sat, 29 May 2004 07:23:37 -0400, "Jeff Morris"
wrote:
Actually, I'd be happy to get 50 or 60 Amps, but some of the advice seems to be
25 Amps might be all I might expect. But the need is for 100 Amps-Hours or
more, so a low current charger is not a good solution if I have to run the
genset 4 hours a day.


========================================

The Xantrex Prosine inverter chargers claim to be corrected for power
factor. I'd call their customer service group, discuss what kind of
generator you intend to use, and ask them to guarantee performance.

http://www.xantrex.com/support/docserve.asp?id=237

In my experience you're much better off with a sine wave inverter
regardless.

  #8   Report Post  
Jeff Morris
 
Posts: n/a
Default On-board generators Revisited

"Wayne.B" wrote in message
...
On Sat, 29 May 2004 07:23:37 -0400, "Jeff Morris"
wrote:
Actually, I'd be happy to get 50 or 60 Amps, but some of the advice seems to

be
25 Amps might be all I might expect. But the need is for 100 Amps-Hours or
more, so a low current charger is not a good solution if I have to run the
genset 4 hours a day.


========================================

The Xantrex Prosine inverter chargers claim to be corrected for power
factor. I'd call their customer service group, discuss what kind of
generator you intend to use, and ask them to guarantee performance.

http://www.xantrex.com/support/docserve.asp?id=237

In my experience you're much better off with a sine wave inverter
regardless.


Yes but that means replacing an expensive piece of equipment with an even more
expensive piece. Frankly, I don't use the inverter much to worry about it - the
microwave seems to do OK, and so does the coffeegrinder. Of course, on the next
boat ...

Actually, it would be neat would be to have a version of the EU1000 that put all
its power out at 14+ Volts, with intelligent charging, of course. Maybe I
should write a letter to Mr. Honda.


  #9   Report Post  
MIDEMETZ
 
Posts: n/a
Default On-board generators Revisited

Take a look at;
http://www.homepower.com/files/mark8.pdf

might be a place to start.

Mike
-----------

Actually, it would be neat would be to have a version of the EU1000 that put
all
its power out at 14+ Volts, with intelligent charging, of course. Maybe I
should write a letter to Mr. Honda.


  #10   Report Post  
surfnturf
 
Posts: n/a
Default On-board generators Revisited


"MIDEMETZ" wrote in message
...
Take a look at;
http://www.homepower.com/files/mark8.pdf

might be a place to start.

Mike


Thanks for the reference to a great site! Good food for thought.

surfnturf


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is Off
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Any Way of testing dash board gauges? g General 1 June 27th 04 04:07 PM
State Police Claims They Can Board Without Probable Cause Capt Lou Cruising 30 April 26th 04 08:27 PM
And the Bush lies just keep on coming basskisser General 81 March 12th 04 12:27 PM
OT Bush: Fair and Balanced jps General 38 March 11th 04 12:39 PM


All times are GMT +1. The time now is 07:40 PM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 BoatBanter.com.
The comments are property of their posters.
 

About Us

"It's about Boats"

 

Copyright © 2017