![]() "Evan Gatehouse" writes: I've been considering the use of Polyfuses (made by Raychem among others) instead of circuit breakers in an electric panel on my boat. They are a lot cheaper (like $0.50 each) and smaller than a breaker. The specs say "100A maximum current" for a typical 5-10A fuse. This is the maximum fault current that can be used to trip such a device. The typical C series Carling hyd./magnetic circuit breaker has a interrupting capacity of 7500A @ 80VDC. This is the toggle type circuit breaker that you see on most new boats. My question: is 100A interrupting enough? If there is a short in a typical wire, will fault currents exceed that? snip What you are asking is really, "What is the short circuit available on this boat?" The answer is dependant on the size of the house bank. 5,000 amps DC would not be considered unusually large. BTW, what you are asking is the answer to a coordination study, something consulting electrical engineers do for a living for large industrial facilities. For the device in question, you need to determine the maximum let thru current under a bolted fault condition. The manufacturer can provide this info. HTH -- Lew S/A: Challenge, The Bullet Proof Boat, (Under Construction in the Southland) Visit: http://home.earthlink.net/~lewhodgett for Pictures |