Fishfinder???
			 
			 
			
		
		
		
			
			The case is not grounded silly. 
 
Cheers 
 
Bobsprit wrote: 
 "MC"  wrote in message 
 ... 
 
Rubbish. 
 
 
 
 Tips on 
 Electrical System Use and Maintenance 
 Part II: High Voltage (AC) Systems 
 by David H. Pascoe, Marine surveyor 
 Full Article 
 
 High Voltage (AC) Systems 
 
 Contents 
 
 Part II 
 
 High Voltage(AC) Systems 
 
 Grounds and Grounding 
 
 Bonding Systems 
 
 Your Bottom Paint 
 
 Electrolysis and Galvanism 
 
 Shore Power Cords 
 
 Polarity 
 
 Main Circuit Protection 
 
 Circuit Breakers 
 
 Chronic Breaker Popping 
 
 GFCI's 
 
 with 0 photos 
 
 Go To Part I 
 
 Introduction 
 with 2 photos 
 
 Part III 
 
 DC Systems 
 with 6 photos 
 
 Part IV 
 
 Adding Electrical Equipment 
 with one photo 
 
 
 
 No one who is not trained in marine high voltage systems should ever perform 
 wiring on a boat. The potential for creating deadly system faults that are 
 injurious to both people and the vessel itself is too risky. That includes 
 something as apparently simple as wiring a new service outlet, for if you 
 don't understand the principles of the system, you are likely to unknowingly 
 create a problem. Just because you know how to do wiring around the house, 
 doesn't mean you know what you're doing on a boat. 
 
 Grounds and Grounding 
 One of the least understood aspects of a boats electrical system, and the 
 most troublesome,  is the proper method of grounding. That we often get 
 questions of whether AC or DC electrical equipment should be grounded to the 
 boat's bonding system is illustrative of this point. AC and DC grounding 
 systems are two separate systems, for distinctly different reasons. If you 
 don't understand these systems, you run the distinct risk of creating a 
 disaster. Actually, there are four separate ground systems: DC ground, AC 
 ground, AC grounding (or bond), and the vessel's bonding system. You can add 
 to this lightning and HF radio grounds as well. Do you know the principles 
 of each? Are you sufficiently confused to discourage you from doing your own 
 wiring? I hope so. For unless you understand each thoroughly, you're headed 
 for trouble. 
 
 The AC ground and grounding systems are "free floating," meaning that they 
 do not ground on the vessel, but only to shore. The ground, or neutral, is a 
 current carrying conductor, and is the source of many troubles because 
 people do not regard it as such. The grounding, bond or green wire is the 
 "safety" intended to channel current safely to ground in the event of a 
 short circuit. Both of these circuits are capable of conducting current and 
 can be the source of electrolysis when there are system faults with the dock 
 or marina wiring. This is very easy to test for. 
 
 There is only one point where the DC side is grounded, and that is at the 
 battery. It, too, is a "free floating" system in which nothing is ever 
 grounded to any metallic part of the vessel, most especially not the bonding 
 system. Just like a car sitting on rubber tires, completely insulated from 
 earth potential, the battery itself provides the negative potential. 
 
 The bonding system, also green wire, has nothing to do with electrical 
 systems. Underwater metals are simply wired together to equalize differences 
 in potential of different kinds of metal. Nothing should ever be grounded to 
 the bonding system. Unfortunately, some people don't understand this and use 
 it to ground electrical equipment, occasionally with disastrous results. 
 
 Bonding Systems 
 Bonding simply means wiring all the boats underwater metals together. This 
 is done because of the galvanism caused by the different metals. By wiring 
 them together, the differing potentials are equalized. Bonding does not 
 solve problems of galvanism or electrolysis, but it does spread the the flow 
 of current around over more metal, so that 1/4 volt or so won't cause any 
 damage. If the Navigator got this far he'd realize that the filter circuit 
 in the ground path (a common mode type) presents an impedance between the 
 transducer ground and the grounding plate. This impedance allows a voltage 
 differential to form and electrolysis to take place. Whereas if that 1/4 
 volt were going to one small seacock, it would probably eat it up in a 
 hurry. In other words, bonding lessens the effect of small amounts of 
 current. On the other hand, it also spreads it around to all underwater 
 metals so that higher currents end up damaging everything. 
 
 Bonding systems use wire and ordinary crimped ring terminals. After a while 
 these get wet and corroded. Electricity doesn't flow very well through 
 corroded metal, so your bonding system after a while stops working. To 
 maintain it, simply cut off the old terminals and install new ones. Do you 
 have wires attached to sea cocks with hose clamps? Forget it. This is 
 putting stainless and copper together, which are galvanically incompatible 
 and it won't work. 
 
 Your Bottom Paint 
 What does bottom paint have to do with electrical systems? Nowadays, with 
 copper based paints, a lot. If, the next time your boat is hauled and you 
 see large ugly burn patterns around all your underwater metals, you got a 
 stray current problem. Copper-based bottom paints react severely to stray 
 current, and serves as a great indicator. Sort of litmus paper for 
 electrical problems. 
 
 Of course, the common wisdom is that the stray current "is from the marina." 
 Or it's always the other guy's boat that is causing your problem. Don't bet 
 on it. Most stray current problems are sourced on the boat in which they 
 appear. Otherwise, everybody in the marina would have the same problem. 
 
 Electrolysis and Galvanism 
 Electrolysis is a word that is badly abused by boaters who don't really know 
 what it means, so let me correct this right now. First, understand that all 
 boats have an electrical potential. That's because of all the different 
 metals on the boat which, themselves have differing electrical potentials. 
 This is exactly the same principle that makes a dry cell battery generate 
 electricity. This electrical potential is called galvanism and is the reason 
 why we put zincs on boats. 
 
 Electrolysis is stray current escaping from the system and is most damaging. 
 It is an abnormal condition. When this happens, it will eat up the zincs in 
 no time, usually leaving that metal looking bright and shiny. Therefo 
 Shiny zincs = electrolysis. Dull eroded zincs = galvanism. 
 
 I spent two years putting a meter on every boat that was hauled for survey. 
 The average boat generates about 1/4 volt DC current and going as high as 
 1/3 volt without causing damage. But when it gets up to 1/2 volt, you got a 
 problem. Zincs will erode rapidly and underwater metals begin to be 
 affected. 
 
 Shore Power Cords 
 The single largest cause of problems with shore power systems results from 
 failure to maintain the connectors on both the cord and the boat connectors. 
 These devices are exposed to water and over time suffer from corrosion and 
 general wear. High resistance caused by corroded, bent or worn connectors 
 results in high resistance which causes overheating, which further amplifies 
 the power drop. This not only creates conditions for a potential fire, but 
 causes electrical equipment to work harder, resulting in reduced life span 
 of equipment. IT PAYS TO MAINTAIN SHORE POWER CONNECTIONS. 
 
 You can perform a very simple check just by placing your hand on the shore 
 cord near the connection to determine if it is heating up. Obviously, this 
 should be done while you have a lot of equipment turned on. If it's anything 
 but slightly warm, not more than 110 degrees, suspect a problem.  Shore 
 power connectors should be dismantled at least once per year, cleaned and 
 repaired as necessary. Most of these connectors have replaceable parts. If 
 you drop your shorepower connector in the water, you must take it apart, 
 clean and dry it. Otherwise, expect it to burn up. 
 
 We recommend that you buy only the highest quality power cords, as these 
 will last longer and have the advantage of replaceable connector parts. 
 Cheap connectors usually can't be taken apart. We also advise against ever 
 using the three-pronger household type adapters as this type of connector is 
 highly unreliable and prone to causing system faults and fires. Only the 
 twist-lock type connector is suitable. 
 
 One more thing: If you are not turning off the dock breaker before 
 disconnecting the power cord, start doing it now. Not only do you risk 
 getting electrocuted, but disconnecting an energized connector damages the 
 contacts. Also consider what happens if you drop the energized cord in the 
 drink! 
 
 Polarity 
 This is an issue only with 125 VAC systems since 250 VAC systems will not 
 function with wrong polarity. Since you have three terminals on a shore 
 connection, wrong polarity can mean that any of these wires are in the wrong 
 position. Not only should you pay attention to the polarity indicator on 
 your boat, we recommend that you keep a plug in polarity indicator aboard 
 and use it every time you hook up to shore power at a different location. 
 
 Reverse polarity is not only an electrocution hazard, but can also damage 
 electrical equipment. It is most often found with the three prong spade 
 connectors (household type), but occasionally twist lock connectors as well, 
 particularly in marinas with dilapidated equipment. Never trust the power 
 supply at strange docks, but always check the polarity. When hooking up to 
 strange docks, always check your volt meters to make sure you have adequate 
 voltage. Low voltage is very damaging to electrical equipment. Turn on the 
 stove or water heater and watch what happens to the meter. 
 
 Main Circuit Protection 
 Many people think that the circuit breakers on the dock protect their boat. 
 They do not; they only protect the dock wiring. Your main circuit breaker 
 protects your boat's systems. But what about that section of wiring and 
 connectors between your main panel and the dock breaker? Well, the fact is 
 that it is unprotected. which is why so many fires occur. Check out all the 
 top end boats and you will find that they have circuit protection located 
 directly at the shore connectors. Which is why we recommend that you should 
 too. Having slow blow cartridge fuses installed directly at the connectors 
 can go a long way toward preventing fires and burned up shore cords, 
 particularly if you are a traveler and frequently rely on uncertain power 
 supplies. Circuit breakers should NEVER be installed on the exterior of the 
 boat. Only gasketed, water proof cartridge holders should be used. 
 
 Circuit Breakers 
 Circuit breakers wear out, and when they do they work less well, or not at 
 all. If you are using circuit breakers as ON/OFF switches, you are helping 
 them wear out that much faster. It also damages breakers when you shut off 
 equipment via the breaker. This causes arcing at the contact points which 
 damages the points. When connecting and disconnecting shore power, you 
 should always turn OFF equipment at the appropriate switch on the equipment. 
 Then shut the main breaker off. Do not ever simply throw the main breaker 
 off to shut down equipment that is operating. The circuit breaker arcs and 
 damages it. 
 
 Also be aware that any equipment run by a motor, such as air conditioning 
 and refrigeration equipment, start up with an initially much higher amperage 
 than the normal running amperage. An air conditioner that runs at 14 amps 
 may have a start up amperage of 20 amps, so that if you just go and turn all 
 the equipment on at once, it overloads the system. Then the circuit breaker 
 gets hot and won't stay engaged until it cools down. Ergo, start up heavy 
 equipment one item at a time, allowing it time to cycle into its normal 
 operating voltage before turning something else on. For example, don't turn 
 the AC, refrigerator and icemaker all on at once and not expect the breaker 
 to pop. 
 
 Chronic Breaker Popping 
 It's human nature that when a problem appears, we wish it to go away. 
 Breakers that pop frequently are signaling that there is a problem, which 
 could either be the breaker, or something in the circuit. Yet most people 
 will keep on attempting to make the breaker engage. This can be dangerous 
 because you may cause the contact points of the breaker to fuse together 
 from arcing, in which case it will never trip again. The above photo shows 
 what can happen when you do this. DO NOT ATTEMPT TO ENGAGE A BREAKER THAT IS 
 OVERHEATED BY FORCING IT. You must allow it to cool down. 
 
 If you are experiencing chronic problems with circuit breakers popping, 
 first check how much current draw is involved. A single 30 amp circuit is 
 not much when you're running things like air conditioners, water heaters and 
 battery chargers. One very simple way to check whether you're dealing with 
 an overload problem is to add up the amperage draw of each piece of 
 equipment. List both the start up and run amperages. You will usually find 
 the amperage given  right on the equipment label. By making a list of the 
 total power demand, you'll get a good idea of what you can and cannot 
 operate simultaneously, particularly when starting the equipment. If you 
 have an ammeter on your panel, check it against the amperage tally you made. 
 Ideally, you should try to hold power consumption at 80% or less than the 
 line rating. 
 
 Check the breaker by allowing it one hour (or whatever it takes)  to cool 
 down. Turn the equipment off and, after it is cool, reengage the breaker. 
 Now turn the equipment back on. Place your finger on the front of the 
 breaker and note its temperature. If it does not heat back up again, then 
 the problem was probably a start-up overload. If the temperature rises 
 again, there is a fault in the circuit or the breaker. (Note: when the 
 breaker contact points become eroded, the breaker itself can overheat). 
 
 GFCI's 
 Ground fault current interrupter service outlets are required to be 
 installed in wet locations such as the galley or head. In reality, there's 
 little chance of being electrocuted inside a boat because you are not 
 grounded within the boat. A greater risk is from service outlets being 
 located in places that get wet, such as below leaking windows, hatches or 
 close to doors. Three pronged plugs are prone to shorting across the 
 terminals when wet, so having all your service outlets changed to GFCI's is 
 a good idea. Use only the highest quality devices from a reliable 
 manufacturer like GE, and not the el cheapos from the local discount store. 
 They aren't worth having. Service outlets located anywhere on the exterior 
 of the vessel are an invitation to trouble for reasons that should be 
 obvious. 
 
 
 
 
 
 
 
 
		 
		
		
		
		
		
		
		
		
			
			
			
			
			
			
			
			
			
			
				
			
			
			
		 
	
	 |