Default Laptop trips GFI

All of my 110 outlets on the boat are protected through GFI. Whenever I plug
my laptop charger in or turn on the computer with it plugged in, it trips
the GFI. If I reset it a time or two or three, it will hold and work fine
until the next time. Interestingly, it will even trip the GFI on a parallel
circuit. I am guessing that it has something to do with the large capacitor
in the charging unit charging up. Does anyone have an explanation and/or
solution?

thanks
john


  #2   Report Post  
chuck
 
Posts: n/a
Default Laptop trips GFI

Obvious questions:

I assume you have GFI outlets and not a GFI breaker.

Anything else plugged in to that outlet when the computer trips the GFI?

Is anything else plugged into the laptop when the GFI trips? SSB? radio?
printer? NMEA stuff?

Have you tested the GFI with the "test" button?

Have you tried the laptop in other GFI outlets?

The only thing that is supposed to trip one is a differential current in
the hot and neutral wires. The unequal current is almost always because
the appliance has found an additional return path through its grounding
conductor back to the service entrance. If such a problem exists with
your laptop, it should be corrected. Alternatively, a new GFI outlet
might cure the problem.

Good luck!

Chuck

johnhh wrote:
All of my 110 outlets on the boat are protected through GFI. Whenever I plug
my laptop charger in or turn on the computer with it plugged in, it trips
the GFI. If I reset it a time or two or three, it will hold and work fine
until the next time. Interestingly, it will even trip the GFI on a parallel
circuit. I am guessing that it has something to do with the large capacitor
in the charging unit charging up. Does anyone have an explanation and/or
solution?

thanks
john


  #3   Report Post  
johnhh
 
Posts: n/a
Default Laptop trips GFI

Thanks, it's the laptop and only the laptop. The only thing I haven't tried
yet is another GI outlet. I need to remember to bring the thing home to do
that. At any rate, it is only a minor inconvenience that will go away after
I wire up the 12v supply I have for it. I just find it curious.

John

"chuck" wrote in message
ink.net...
Obvious questions:

I assume you have GFI outlets and not a GFI breaker.

Anything else plugged in to that outlet when the computer trips the GFI?

Is anything else plugged into the laptop when the GFI trips? SSB? radio?
printer? NMEA stuff?

Have you tested the GFI with the "test" button?

Have you tried the laptop in other GFI outlets?

The only thing that is supposed to trip one is a differential current in
the hot and neutral wires. The unequal current is almost always because
the appliance has found an additional return path through its grounding
conductor back to the service entrance. If such a problem exists with your
laptop, it should be corrected. Alternatively, a new GFI outlet might cure
the problem.

Good luck!

Chuck

johnhh wrote:
All of my 110 outlets on the boat are protected through GFI. Whenever I
plug my laptop charger in or turn on the computer with it plugged in, it
trips the GFI. If I reset it a time or two or three, it will hold and
work fine until the next time. Interestingly, it will even trip the GFI
on a parallel circuit. I am guessing that it has something to do with
the large capacitor in the charging unit charging up. Does anyone have
an explanation and/or solution?

thanks
john



  #4   Report Post  
Larry
 
Posts: n/a
Default Laptop trips GFI

If it has 3-wire grounded plug on it, plug it into a ground buster and see
if it stops. The input filters on some of the switching supplies allows
enough AC to ground pin to trip them. I've had some ground loops trip mine
here at home from certain printers plugged into the outlets on other
circuits than what the computer is plugged into.

"johnhh" wrote in
:

All of my 110 outlets on the boat are protected through GFI. Whenever
I plug my laptop charger in or turn on the computer with it plugged
in, it trips the GFI. If I reset it a time or two or three, it will
hold and work fine until the next time. Interestingly, it will even
trip the GFI on a parallel circuit. I am guessing that it has
something to do with the large capacitor in the charging unit charging
up. Does anyone have an explanation and/or solution?

thanks
john






--
Larry
  #7   Report Post  
johnhh
 
Posts: n/a
Default Laptop trips GFI

Good idea, I'll try that.

"Larry" wrote in message
...
If it has 3-wire grounded plug on it, plug it into a ground buster and see
if it stops. The input filters on some of the switching supplies allows
enough AC to ground pin to trip them. I've had some ground loops trip
mine
here at home from certain printers plugged into the outlets on other
circuits than what the computer is plugged into.

"johnhh" wrote in
:

All of my 110 outlets on the boat are protected through GFI. Whenever
I plug my laptop charger in or turn on the computer with it plugged
in, it trips the GFI. If I reset it a time or two or three, it will
hold and work fine until the next time. Interestingly, it will even
trip the GFI on a parallel circuit. I am guessing that it has
something to do with the large capacitor in the charging unit charging
up. Does anyone have an explanation and/or solution?

thanks
john






--
Larry



  #8   Report Post  
chuck
 
Posts: n/a
Default Laptop trips GFI

A ground buster would be one way to check for excessive leakage to
ground. But exercise caution: the GFI is tripping either because it is
defective or because there is a potentially dangerous leakage. We tend
to immediately suspect a more or less constant borderline leakage such
as might occur in the case of a defective or poorly designed filter as
Larry suggests. Or it could be a less-likely but very serious
intermittent condition like a short. If so, with a ground buster in the
circuit, your body could well supply the leakage path to ground.

But most of the chargers use 2-wire, "polarized" ac cords in which case
the ground buster would have no effect. With a 2-wire cord and a
properly functioning GFI and nothing else plugged into the receptacle or
the computer, a trip can occur only if you provide the path to ground.
If it trips while you are not touching it and it is fully insulated from
the boat's ac ground, the GFI is probably defective.

You still haven't told us if your GFI is a breaker type in the main
panel or a receptacle. If the latter, why not just plug the computer
into one of the other protected outlets on the boat? If the former,
complex grounding or wiring situations could cause the problem.

Good luck.

Chuck

Larry wrote:
If it has 3-wire grounded plug on it, plug it into a ground buster and see
if it stops. The input filters on some of the switching supplies allows
enough AC to ground pin to trip them. I've had some ground loops trip mine
here at home from certain printers plugged into the outlets on other
circuits than what the computer is plugged into.

"johnhh" wrote in
:


All of my 110 outlets on the boat are protected through GFI. Whenever
I plug my laptop charger in or turn on the computer with it plugged
in, it trips the GFI. If I reset it a time or two or three, it will
hold and work fine until the next time. Interestingly, it will even
trip the GFI on a parallel circuit. I am guessing that it has
something to do with the large capacitor in the charging unit charging
up. Does anyone have an explanation and/or solution?

thanks
john







  #9   Report Post  
johnhh
 
Posts: n/a
Default Laptop trips GFI

--It is a GFI receptacle, not a breaker.
--The charger (110AC to 18.5v DC) has a 3 wire plug.
--It only occurs with the laptop and always occurs with the laptop
--It makes no difference what else is connected to the laptop or AC.
--It occurs whenever the computer is turned on or the charger is plugged
into an already running computer.
--It always recovers after one to three resets.
--It is far too consistent to be an intermittent condition like a short.
--It usually, but not always, trips both the GFI it is plugged into and the
other one on a parallel circuit.
--I have two different AC circuits off of the same breaker but each
protected by a GFI outlet. I am not sure of the exact wiring of these as I
haven't traced the wires down.

--No matter how much information I think I give or imply, I always seem to
leave something out.

--I'll try it on the second GFI on the boat, but will be very surprised if
it works there.
--I'll bring it to the house at the next opportunity and try it there.
--I'll try a ground buster.

I am of the belief that there is really nothing wrong with anything.
Larry's induced current theory sounds reasonable. These chargers have a
very large capacitance that take a second or so to charge up. I believe it
has to do with that charging somehow.



"chuck" wrote in message
news
A ground buster would be one way to check for excessive leakage to ground.
But exercise caution: the GFI is tripping either because it is defective or
because there is a potentially dangerous leakage. We tend to immediately
suspect a more or less constant borderline leakage such as might occur in
the case of a defective or poorly designed filter as Larry suggests. Or it
could be a less-likely but very serious intermittent condition like a
short. If so, with a ground buster in the circuit, your body could well
supply the leakage path to ground.

But most of the chargers use 2-wire, "polarized" ac cords in which case
the ground buster would have no effect. With a 2-wire cord and a properly
functioning GFI and nothing else plugged into the receptacle or the
computer, a trip can occur only if you provide the path to ground. If it
trips while you are not touching it and it is fully insulated from the
boat's ac ground, the GFI is probably defective.

You still haven't told us if your GFI is a breaker type in the main panel
or a receptacle. If the latter, why not just plug the computer into one of
the other protected outlets on the boat? If the former, complex grounding
or wiring situations could cause the problem.

Good luck.

Chuck

Larry wrote:
If it has 3-wire grounded plug on it, plug it into a ground buster and
see if it stops. The input filters on some of the switching supplies
allows enough AC to ground pin to trip them. I've had some ground loops
trip mine here at home from certain printers plugged into the outlets on
other circuits than what the computer is plugged into.

"johnhh" wrote in
:
All of my 110 outlets on the boat are protected through GFI. Whenever
I plug my laptop charger in or turn on the computer with it plugged
in, it trips the GFI. If I reset it a time or two or three, it will
hold and work fine until the next time. Interestingly, it will even
trip the GFI on a parallel circuit. I am guessing that it has
something to do with the large capacitor in the charging unit charging
up. Does anyone have an explanation and/or solution?

thanks
john






  #10   Report Post  
Larry
 
Posts: n/a
Default Laptop trips GFI

"johnhh" wrote in
:

I am of the belief that there is really nothing wrong with anything.
Larry's induced current theory sounds reasonable. These chargers have
a very large capacitance that take a second or so to charge up. I
believe it has to do with that charging somehow.



I'm also leaning, because it trips a GFI it's not connected to, that the
switcher is sending lots of RF noise back up the power line. Take a small
portable AM radio and put it near the power supply. Tune up and down the
band and listen for "hash" when the supply is plugged in. The hash fed
back into the GFI may also be what's tripping it...and the other one.
Terrible designs do make it to market from China.

--
Larry
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is Off
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 11:34 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 BoatBanter.com.
The comments are property of their posters.
 

About Us

"It's about Boats"

 

Copyright © 2017